Does 690.64 (B)(7) (NEC 2008) mean that the back fed breaker can not be next to the main breaker and has to be as far away from the main as possible?
I believe the bolded section does not refer to the main service disconnect. Does it?
Thank you.
(7) Inverter Output Connection. Unless the panelboard is
rated not less than the sum of the ampere ratings of all overcurrent
devices supplying it, a connection in a panelboard
shall be positioned at the opposite (load) end from the input
feeder location or main circuit location. The bus or conductor
rating shall be sized for the loads connected in accordance
with Article 220. In systems with panelboards
connected in series, the rating of the first overcurrent device
directly connected to the output of a utility-interactive
inverter(s) shall be used in the calculations for all busbars
and conductors. A permanent warning label shall be applied
to the distribution equipment with the following or equivalent
wording:
I believe the bolded section does not refer to the main service disconnect. Does it?
Thank you.
(7) Inverter Output Connection. Unless the panelboard is
rated not less than the sum of the ampere ratings of all overcurrent
devices supplying it, a connection in a panelboard
shall be positioned at the opposite (load) end from the input
feeder location or main circuit location. The bus or conductor
rating shall be sized for the loads connected in accordance
with Article 220. In systems with panelboards
connected in series, the rating of the first overcurrent device
directly connected to the output of a utility-interactive
inverter(s) shall be used in the calculations for all busbars
and conductors. A permanent warning label shall be applied
to the distribution equipment with the following or equivalent
wording: