NEC says to use inverter output amps if provided, in calcs for sizing the PV breaker.
Why does the new SMA TL series show such high amps on the spec sheet?
I mean what is the technical reason behind it, not legal or code compliance?
How can - for example the 4000 W inverter - generate 20 Amps, at 240 Volts AC??
The spec sheet itself shows its AC output limited to exactly 4000 Watts.
3000: 15 A
4000: 20 A
5000: 22 A
I would have assumed
12.5 A
16.66... A
20.83 A
It looks like they figured out the minimum breaker size you would otherwise get, if you just divided output W by VAC and then bumped up the amps to the max within that breaker's limits.