why would an electrical conduit get hot

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
wires in conduit are not hot!!!
Non-zero net current flowing in the wires inside a ferromagnetic (iron, steel) conduit will cause inductive heating in the metal of the conduit. But that normally requires a pretty high current to be noticeable.
Also if the conduit is being used as an EGC, a high ground current (not normal) could be causing resistive heating.
Use a clamp-on ammeter to measure net current in wires and in wires plus conduit (put the clamp-on around the whole thing) and then figure out whether the problem is a missing neutral run or different phases and their returns being split over more than one conduit.
 

iwire

Moderator
Staff member
Location
Massachusetts
Non-zero net current flowing in the wires inside a ferromagnetic (iron, steel) conduit will cause inductive heating in the metal of the conduit. But that normally requires a pretty high current to be noticeable.


Or in layman's terms the goes into and the goes out of are not equal. :)
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Please define hot. The normal current flow in any conductor will produce heat. It is not too hot unless the conductors are at a temperature higher than their temperature rating. The lowest commonly used temperature rating for conductors is 140?F. That will be hot to the touch.
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I've seen 80% loaded conductors cause a conduit to get warm. And it has been warm for years. 90 degree's F.

Note that the OP states that the wires are not hot but the conduit is hot. I am assuming that means that the wires are not as hot as the conduit and so it is not possible that they are the sole source of the conduit itself heating up.
 

Besoeker

Senior Member
Location
UK
Note that the OP states that the wires are not hot but the conduit is hot. I am assuming that means that the wires are not as hot as the conduit and so it is not possible that they are the sole source of the conduit itself heating up.
Agreed.
I'd go for earth fault or more likely inductive heating from unbalanced current.
 

templdl

Senior Member
Location
Wisconsin
I have to agree with Don who has made an excellent point, please define what you mean as being hot. Quite often anything that is expected to be cool to the touch quite often is referee to as being hot should it be only warm to the touch. When referring to heat the temperature should be provided so there is no misunderstanding as it is relative. Wires that are loaded do give off heat.
The same thing happens with sound. When you expect something to be quiet and it's giving off sound often it's considered as being noisy. Db sound level should be provided when referring to noise.
 

Besoeker

Senior Member
Location
UK
Wires that are loaded do give off heat.
But, in this case according to the OP, are not hot.
A reasonable inference, as has been previously stated, is the conductors are not the source or at least not the sole source.
 

junkhound

Senior Member
Location
Renton, WA
Occupation
EE, power electronics specialty
wires in conduit are not hot!!!

+1 on all the previous comments about giving good data when you refer to any phenomenon, whether heat, electricity, or noise.

Do you mean the wires that are comong OUT of the conduit are not hot? How did you get inside the conduit to measure wire temp IN the conduit?

What did you measure 'hot' with? Hand, thermocouple, IR device? If by human skin measurement, it could be HF leakage current interpreted as 'heat', if thermocouple it could be EMI, if IR device it cold be pointing error.

Is there a VFD or inverter at the load end?
 
Last edited:

renosteinke

Senior Member
Location
NE Arkansas
I observed the same thing when I took part in wiring one of those huge mail-order warehouses. I sure I could have circled the earth several times with all the wire I pulled.

The point is that, even without an 'load' to speak of, but with all the circuits powered up, SOME raceways were noticeably warmer than neighboring conduit. These pipes contained wires for a multitude of sensors, readers, and solenoids - everything went to the PLC cabinet.

Fast forward to today, where I daily deal with "wires" that stay rather cool (maybe 'only' 180 degrees F) while they make neighboring steel hot enough to glow and even melt.

The secret lays in the fluctuating magnetic field of the electricity flowing through the wires. It's not current, really - it's much more about frequency. Kick the frequency up to a few thousand cycles, and nearby steel starts getting hot.

This is the same principle used in the new "induction" ranges - where the pot gets hot, but the cooktop does not. (Well, not as hot as the pot does!)
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
I observed the same thing when I took part in wiring one of those huge mail-order warehouses. I sure I could have circled the earth several times with all the wire I pulled.

The point is that, even without an 'load' to speak of, but with all the circuits powered up, SOME raceways were noticeably warmer than neighboring conduit. These pipes contained wires for a multitude of sensors, readers, and solenoids - everything went to the PLC cabinet.

Fast forward to today, where I daily deal with "wires" that stay rather cool (maybe 'only' 180 degrees F) while they make neighboring steel hot enough to glow and even melt.

The secret lays in the fluctuating magnetic field of the electricity flowing through the wires. It's not current, really - it's much more about frequency. Kick the frequency up to a few thousand cycles, and nearby steel starts getting hot.

This is the same principle used in the new "induction" ranges - where the pot gets hot, but the cooktop does not. (Well, not as hot as the pot does!)

It is about the hysteresis losses in the iron, which for a given time interval will be proportional to the current times the frequency.
Even at high frequency, if the currents are balanced and ideally in twisted pairs, there will be no inductive heating.
An inductive range uses a multi-turn coil around the core. Inductive heating in a conduit will be at most a single turn.a
 

kwired

Electron manager
Location
NE Nebraska
An inductive range uses a multi-turn coil around the core. Inductive heating in a conduit will be at most a single turn.a

and in the conduit with properly installed conductors or "turns" there is equal number opposing polarity turns which cancel one another out. If every turn of the coil in the inductive range were to have an opposing polarity and same magnitude turn wrapped around the same core it would not transfer any significant amount of heat to the pot. There probably would be some inefficiencies and some heat, but not enough to be considered effective for the purpose of heating the pot as desired.
 

hurk27

Senior Member
Wouldn't the bonding of the primary X/0 on a step up 3-phase common core transformer cause enough current in the grounding if the secondary is not balanced, but not heat the phase conductors?
 

kbsparky

Senior Member
Location
Delmarva, USA
I've seen instances where a load management system was installed with lots of single-wires going through the same nipple causing the conduit to get noticeably warm.
 

Jraef

Moderator, OTD
Staff member
Location
San Francisco Bay Area, CA, USA
Occupation
Electrical Engineer
I only seen a hot conduit once where a contractor had tried to pull isolated parallel phases in EMT like we do with PVC, he didn't know it would be a problem, but that was a long time ago.
First thing that came to my mind too. 3 phase installation requiring parallel conductors, but done by an amateur having one conduit holding all Phase A, one with Phase B, one with Phase C, instead of one of each phase in each conduit.
 

kwired

Electron manager
Location
NE Nebraska
I've seen instances where a load management system was installed with lots of single-wires going through the same nipple causing the conduit to get noticeably warm.
was line side and load side of each circuit passing thru the same nipple? Even one common line conductor and several switched load conductors still has cancelling effect as the line conductor is carrying the same current as the sum of the load conductors.
 

kbsparky

Senior Member
Location
Delmarva, USA
There were 2 nipples:

One for "line"

The other one for "load"

Needless to say, those 2 foot sections of EMT were quite hot to the touch ...
 