There is some confusion about the sizing of neutral service conductors.
When a large % of the loads are 240 or 208 volt and neutral calc is very low.
NEC tell us that regaurdless of load the neutral or (grounded conductor) can not be smaller then the EGC 215.2(A)(2) per Tbl.250.122
220.61 (A) tells us that the max unbalanced load shall be the max net calculated load between the neutral and any one ungrounded conductor.
So if I have a 200 amp single phase service with 121 amps on line one and 96 amps on line two.
Do I size the neutral to carry
A. The 121 amps on line one (even though much of the load is 240 volt) # 1Cu. Tbl. 310.15(B)(16)
B. My calculated load of 86 amps? # 4 Cu. Tbl 310.15(B) (16)
C. Or by Tbl 250.122 200A = #6 Cu.