Thank you for reply, I don't I trying to understand this question......Question only ask for the de-rating percentage value for 8 current carrying conductors in a cord or cable. very confuse for me..
Forgive my first reply, I don't think I understood just what you were asking at that time.
The use of 400.5(A)(3) is no different than using 310.15(B)(3)(a) except it applies to flexible cords instead of cables and raceways.
Your question mentioned 8 current carrying conductors, doesn't really matter at this point what those conductors are supplying or how many other "non current carrying conductors" may also be in the same cord.
The title of the table even kind of explains a little - "for more than three current carrying conducotors".
For three or less "current carrying" conductors, no additional adjustment is necessary. For three or more, use the adjustment factors in the table. The reason for adjustment is the heat produced within the conductors - the more current carrying conductors there are the more heat there will be, but larger conductors will have less resistance and will give up less heat. It is all about protecting the conductor insulation from overheating. You do not ignore the first three when counting the total number of current carrying conductors.