dry type transformer

Status
Not open for further replies.

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
how do i wire a 45kva 3p 208/ 208 120 transformer? do i make a case bond to the xo bar? do i need a neutral from my primary feed?
You appear to be describing a delta to wye transformer. Is the delta side the input? So the X0 lead would be on the secondary side?

If the primary is delta, you do not need a primary neutral, but you must provide a ground/EGC bonded to the secondary neutral.
 