Outlets in laundry room
augie47
Tennessee
Is there a laundry sink ?
Although, not to NEC standards, there were some jurisdictions that would allow a single receptacle in lieu of a GFCI within 6 ft of a laundry sink.
Gregg Harris
Virginia
Electrical,HVAC, Technical Trainer
The circuit must serve only laundry areas - an area is not a piece of utilization equipment, and the laundry circuit is not an individual branch circuit.
The outlet is not to serve the laundry area, but the laundry equipment.
At least one 120 volt 20 amp circuit is required in the laundry area to serve the laundry equipment with no other outlet on the circuit.
If it is a single receptacle only one outlet is provided and should be rated at 20 amps.
If it is a duplex or triplex or quad etc. multiple outlets would be provided on the circuit that specifically states "no other outlets"
GoldDigger
Placerville, CA, USA
Retired PV System Designer
You could make the argument that a single duplex receptacle is one outlet, since it is at a single point on the wiring system. Not sure how far that would fly though. :)
ActionDave
Chief Moderator
Licensed Electrician
I agree with George also. There is no requirement that the circuit be for the laundry equipment only the laundry area. It can have no other outlets the same way a SABC can have no other outlets.
Besides, I'm pretty sure the requirement pre-dates the electric washing machine.