When ever this subject has been brought up one is to be reminded that even though neutrals a commonly grounded you can not use a grounded neutral to short cut the need for an EGC. I do realize that the older 3w appliance circuits have been grandfathered in where the neutral and ground conductor are combined, a practice which is not allowed to be used today.
The neutral carried the unbalance current and as such is a current carrying conductor. Usind the nuetral grounded conductor at any point down steam from the the point that it is grounded at the service entrance will allow any devices that use the grounded neutral as a grounding point to be exposed to the neutral current. Thus it exposes anyboby who is touching a device that is supposed to grounded to a potential shock hazzard. As a reminder GFCIs have a 5ma sensitivity. If you are using this method to ground and electric tool with a metal case for example can you be guaranted should someone be using the tool would not be exposed to any current higher than 5ma? I think not.