Can (1) ATS be used to supply loads of Article 701 & 702 as long as the Generator is sized for the full load of the Article 700, 701 & 702 Systems in an Office Building?
I cannot find anything that says it cannot be installed with the following scenario
1.) (1) ATS for the Article 700 Loads
2.) (1) ATS for the Article 701 & 702 Loads combined - 701 Loads are Stair Pressurization & Elevator Loads, 702 Loads are I.T. Closets and a few Receptacles
3.) Generator Sized for all loads at once.
I am being told be the engineer that we are required to provide (3) separate ATS's.
Thanks