Busway Feeder size

Status
Not open for further replies.

John Dundon

Member
Location
CT
I am currently feeding a 480V 3-wire 400 amp busway with set of parallel 3/0 THHN conductors which gives me a total ampacity of 400A @ 75 deg. The busway is providing power to various CNC machines. Do I have enough copper?
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
Baring some unforeseen element such as ambient or voltage drop, I see no problem.
 

John Dundon

Member
Location
CT
First timer and I like this forum.

First timer and I like this forum.

Thank you for the input. I had one of those over thinking it moments. I was thinking that because the loads of this busway had motors that I would need to be 125% for the feeders to the buss. I will do that calc from the busheads to each machine.:thumbsup:
 

ron

Senior Member
Thank you for the input. I had one of those over thinking it moments. I was thinking that because the loads of this busway had motors that I would need to be 125% for the feeders to the buss. I will do that calc from the busheads to each machine.:thumbsup:
The Busway is part of the feeder so if the busway is 400A, then the conduit/wire should be 400A
 