caculating j box size

Status
Not open for further replies.

SparkyRules

Member
Location
United States
I want to run 4-4" conduits in one side of a j-box (314.28-(A)(1)=8x largest raceway or 4"x8=32 " minimum. However out the other side I want to attach a 8" duct(Art376). would the 8" duct be considered a raceway if so then I would need 8x8 or a 64" J box? Comments?
 

kingpb

Senior Member
Location
SE USA as far as you can go
Occupation
Engineer, Registered
I assume the 4" conduits are carrying 4 sets of parallel conductors the duct you mention is actually wireway.

Therefore the MINIMUM distance from the side where the conduits enter to the opposite side with the wireway is the 32" you mention.

However, I think a question arises that the cables can only take up 20% of the cross sectional area of the wireway. Hence, 8" x 8" = 64 sqin; 20% is 12 sqin

If the 4 x 4" conduits are all filled to maximum 40%, then you have 20 sqin of conductors and the 8" x 8" wireway is not sufficient.

Something to consider.
 

jusme123

Senior Member
Location
NY
Occupation
JW
...a wireway is considered a raceway.


what is being pulled through the 4" conduits?
 