Sheet Metal Junction Box Fill

Status
Not open for further replies.

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Where the conductors are #4 and larger, the size of the box is based on the size of the conduit entries. There is no volume calculation for boxes with #4 and larger conductors. See 314.28.
 

msteiner

Senior Member
Location
Maryland
That's what I was looking for, thanks. I had already sized my box per 314.28, but wanted to make sure there wasn't a separate fill calculation.
 