Where can I find the box fill requirements for a large sheet metal JB (24"x24"x42")?
M msteiner Senior Member Location Maryland Sep 19, 2013 #1 Where can I find the box fill requirements for a large sheet metal JB (24"x24"x42")?
raider1 Senior Member Staff member Location Logan, Utah Sep 19, 2013 #2 What size conductors are going to be installed in said J-box? Chris
M msteiner Senior Member Location Maryland Sep 19, 2013 #3 Ten three-phase circuits total, from 100A - 225A, all being spliced.
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Sep 19, 2013 #4 Where the conductors are #4 and larger, the size of the box is based on the size of the conduit entries. There is no volume calculation for boxes with #4 and larger conductors. See 314.28.