Transformer size

Status
Not open for further replies.

iwire

Moderator
Staff member
Location
Massachusetts
were in the NEC does it specify anything about xfmr sizing?

I don't think it does.

But I work in the real world with real inspectors and there is no way they would allow a calculated greater than the rating of the transformer.


At the least they could cite 110.3(A)(7).
 
I have the answer buts its easy to screw up depending on how you calculate it. I=kvax1000 divided by 208x1.73. I made the mistake of multiplying 208x1.73=359.84. 1000kva =1,000,000 divided by 359.84=2779.012 but this is actually incorrect. You have to do the formula in order. 300kva is the correct answer because if you do the formula in order it comes out quite different. 300,000 divided by 208=1442.30x1.73=2495.19. By doing it in my head in 2 parts I managed to look like an idiot yesterday. Thanks to all who chimed in though. Remember kids, do your formulas in order.
 

JDBrown

Senior Member
Location
California
Occupation
Electrical Engineer
I have the answer buts its easy to screw up depending on how you calculate it. I=kvax1000 divided by 208x1.73. I made the mistake of multiplying 208x1.73=359.84. 1000kva =1,000,000 divided by 359.84=2779.012 but this is actually incorrect. You have to do the formula in order. 300kva is the correct answer because if you do the formula in order it comes out quite different. 300,000 divided by 208=1442.30x1.73=2495.19. By doing it in my head in 2 parts I managed to look like an idiot yesterday. Thanks to all who chimed in though. Remember kids, do your formulas in order.
Um... I'm not sure I understood all that, but the way to calculate this is:

(208V x 1.73 x 2400A) / 1000 = 864 kVA

Which is why Mr. iwire said your transformer should be at least 870 kVA. So you did it right yesterday. You only get 300 kVA if you divide by 1.73 instead of multiplying by it, which is not the way you calculate kVA.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
Um... I'm not sure I understood all that, but the way to calculate this is:

(208V x 1.73 x 2400A) / 1000 = 864 kVA

Which is why Mr. iwire said your transformer should be at least 870 kVA. So you did it right yesterday. You only get 300 kVA if you divide by 1.73 instead of multiplying by it, which is not the way you calculate kVA.

For some people, the calculation is easier to remember as just 120x2400x3, as if the setup were wye, because the power going through the three phase wires is exactly the same whether it is going to a balanced delta or balanced wye load at 2400A per line.
You can demonstrate that the formula is exactly the same because 208 = 1.73 x 120 and 1.73 x 1.73 = 3.

So 2400 x (120 x 3) is exactly equal to 2400 x (208 x 1.73).

If you are given that the supply is 2400A 208 delta instead of 2400A 208Y/120, then the other way is simpler to compute but harder to remember for me.
 