I did a site visit today for a commercial property and the AHU's are on the 480V panel but listed as 208 on the name plate.. Has anyone else ever came cross something like this??
You sure about that? Is there a transformer along the way?
I did a site visit today for a commercial property and the AHU's are on the 480V panel but listed as 208 on the name plate.. Has anyone else ever came cross something like this??
Yes sir. It is a 225Amp 480V panel--25kva transformer--225amp 208v panel bussed @ 150amps
To be fair to the EE's, this is just as likely (if not more so) to be the HVAC guy's mistake. We always coordinate the electrical requirements with the ME, but it seems like about half the time (okay, that's an exaggeration) when the EC goes to connect power to the HVAC unit he discovers it's the wrong voltage. The EE, ME and EC are all on the same page, but whoever ordered the HVAC equipment ignored the drawings and bought units with the wrong voltage (or they bought single phase units instead of 3-phase).What we have here is a failure to communicate.
That transformer is a bandaid on somebody's coordination booboo. I don't know why EE's don't take the initiative to communicate to the mech dept/contractor/consultant what voltage they need for the equipment they are supplying. Except in very rare circumstances, the units are available at whatever voltage you need them to be, and the EE knows best which voltage to use.
I have worked with designers who just take for granted that the mechanical people know what they are doing, voltage wise. They don't. You have to tell them what to use.
Yes sir. It is a 225Amp 480V panel--25kva transformer--225amp 208v panel bussed @ 150amps