Just example, We have a service panel feeds chiller and another panel. The chiller load is 400kva (non-continous load) & the other panel is 100kva (50% continous load). The ocpd of the chiller is 1000a and for the panel is 200a.
The ocpd of service panel will be:
If applies (1.25*continous+1*non continous+0.25*largest motor)/400/1.73
(1.25*50kva+1*450kva+0.25*70kva (largest motor inside the chiller))/400/1.73=766a
the OCPD will be 800a
By comparing chiller ocpd 1000a vs 800a for the service panel, what is the best we can do here?