bradleymattlin
Member
- Location
- Airville, PA
I have 3 sets of 3/0 copper parallel feeders coming in from a CT cabinet, thru a trough and into a 400 amp distribution panel. My tap is for 100 amps and using number 1 copper and going to tap off one leg of A phase and one leg of B phase and a neutral to give my 120/208. My tap is under 10 feet and all rules apply for 240.21. Can someone explain to how the 3/0 copper that iam tapping into doesn't have to be bigger and handle the load of the new tap, or maybe it doesn't work that way and its just voltage. Thanks