Is this 1 unit or 2?
darekelec
nyc
Should I run 1 or 2 15 amp circuits?
I am asking cause my boss is on vacations.
thx
GoldDigger
Placerville, CA, USA
Retired PV System Designer
I'd vote (1)
Looks that way to me too. One 15A 3-phase circuit. They may have several contactors in it for some reason, but the number of fans visible is consistent with the nameplate value for one unit. (Not quite sure where they are hiding the third fan, but....)
don_resqcapt19
Illinois
retired electrician
If you run two circuits you will need two disconnects at the unit and the internal control circuit will probably be fed by one of your circuits. If you lose the circuit that feeds the controls. both units will be non-functioning. I think, based on the nameplate, you could make a case for a 110.3(B) violation if you ran two circuits to the equipment.
StarCat
Industrial Engineering Tech
Moab, UT USA
Imdustrial Engineering Technician - HVACR Electrical and Mechanical Systems
Remote condenser
Remote condenser
Typically the older units would have had a terminal block feeding both those contactors.
Heatcraft appears to have gotten cheap and they are expecting you to jumper for the line feeds.
I would call and ask them whats up and note the response you get.
You might be amazed at what kind of people are drawing paychecks these days and exactly what they do for such.
augie47
Tennessee
I hear that on some of my inspections :D