bonding conduits in a transformer

Status
Not open for further replies.
Sorry I just couldn't resist - ignore my last response. In terms of equipment grounding/bonding a transformer is just another piece of equipment. Whether a bonding bushing is required would depend on the voltage, if it has concentric knockouts, and if the knockouts are listed for grounding. In short I would say combine the first to responses to "maybe, probably no"
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Yes, probably not is true, but we have no information about the installation. For all we know it may be a pad mount transformer.
 