grounding

Status
Not open for further replies.
NEC requires 25 ohms for effective ground. If single 10 feet ground rod does not meet the requirement, can it be augmented by additional rod by threaded coupling on the top of existing rod, by driving the previous rod further down by 10 more feet? NEC is silent about maximum distance.
Please help, or suggest alternate method of improving ground resistance outdoor (no structural steel, or water pipe available).
Thanks
Kaushal
 

david luchini

Moderator
Staff member
Location
Connecticut
Occupation
Engineer
NEC requires 25 ohms for effective ground. If single 10 feet ground rod does not meet the requirement, can it be augmented by additional rod by threaded coupling on the top of existing rod, by driving the previous rod further down by 10 more feet? NEC is silent about maximum distance.
Please help, or suggest alternate method of improving ground resistance outdoor (no structural steel, or water pipe available).
Thanks
Kaushal

The NEC says that the additional rod shall be installed not less than 6' apart from the first rod. See 250.56.
 
NEC requires 25 ohms for effective ground. If single 10 feet ground rod does not meet the requirement, can it be augmented by additional rod by threaded coupling on the top of existing rod, by driving the previous rod further down by 10 more feet? NEC is silent about maximum distance.
Please help, or suggest alternate method of improving ground resistance outdoor (no structural steel, or water pipe available).
Thanks
Kaushal

David is right.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
NEC requires 25 ohms for effective ground. If single 10 feet ground rod does not meet the requirement, can it be augmented by additional rod by threaded coupling on the top of existing rod, by driving the previous rod further down by 10 more feet? NEC is silent about maximum distance.
Please help, or suggest alternate method of improving ground resistance outdoor (no structural steel, or water pipe available).
Thanks
Kaushal

there is no requirement that a ground rod be 10' long nor is there a requirement for 25 Ohms.

a ground rod has to be only 8' long [250.52(A)(5)].

the 25 Ohms thing only comes into play if there is only one ground rod [250.53(A)(2)exception]. If you pound in 2 rods and it is 100 Ohms, that is fine with the code.

250.53(A)(3) requires supplemental electrodes (if required) to be not less than 6 feet apart. I suppose that if you threaded 3 ten foot long rods together and pounded them in you could make a reasonable claim that there were two rods at least 6 feet apart.
 
Last edited:

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
there is no requirement that a ground rod be 10' long nor is there a requirement for 25 Ohms.

a ground rod has to be only 8' long [250.52(A)(5)].

the 25 Ohms thing only comes into play if there is only one ground rod [250.53(A)(2)exception]. If you pound in 2 rods and it is 100 Ohms, that is fine with the code.

250.53(A)(3) requires supplemental electrodes (if required) to be not less than 6 feet apart. I suppose that if you threaded 3 ten foot long rods together and pounded them in you could make a reasonable claim that there were two rods at least 6 feet apart.

My impression is that the OP is also concerned with whether it would be OK to drive the original single rod deeper (using extensions) and then measure a resistance less than 25 ohms.
The code does not put any restriction on the maximum length of a rod electrode, so if driving the "failed" rod deeper got it below the 25 ohm limit, it would remove the need to drive a second ground rod regardless of the position.
I could see this being an attractive option if there were not enough free dirt space to drive a second rod meeting the separation requirements and no good opportunity for another type of supplemental electrode.
If you put the original rod in the middle of a 10 foot diameter opening in the concrete, then you could not just drive a second rod, you would have to drive two so that the separation between those two could be 6 feet or more.

Depending on the soil conditions, the single deeper rod could also provide a better ground, although the code does not care about that. Soil conditions where you could drive the rod 10 feet deeper would probably also be ones where the additional depth would help.

Only concern i would have is whether the threaded or screw coupling would be recognized as a good enough connection between the two rod sections. (Cadweld anyone?)
You could attach the GEC to the top of the lower rod section before driving it down I suppose.
 
Last edited: