Is it acceptable to use SER cable above a drop ceiling. I'm trying to feed a sub panel located roughly 200ft from the main panel in a commercial setting. If not SER, what would be the appropriate cable?
Look at 334.12(A)(2) which is directed from 338.10(B)(4). Mc cable would work
Look at 334.12(A)(2) which is directed from 338.10(B)(4). Mc cable would work
do they even make MC that big??? i need it to be like #4 (100 amp sub panel)
do they even make MC that big??? i need it to be like #4 (100 amp sub panel)
#4 for 100 amperes in a non-residential setting?
Good catch, I missed that.
Even in resi, #4 CU is no good for a sub panel.
That is how I took it.