Can and should 5/16" flex metal conduit be used to install undercabinet, line-voltage
direct-wired lights/luminaries?
Background
Kitchen remodel and I'm the general contractor. I do not do any electrical work myself - the reason I ask this question is that my electrician is a little lazy and tends to use whatever materials are on his truck instead of making a trip to the electrical supplier to purchase and install the most appropriate materials for the application. Before he starts his final electrical work, I want to specify how and what materials should be used to hook-up the lights. Thus, I have a few questions regarding RWA FMC, line-voltage, direct-wire Zenon lights will be installed under the cabinets. I had the electrician make 14-2 drops at every fixture location. 14-2 wires are tied back into a j-box and are on a dedicated lighting circuit. I am aware that the 14-2 Romex needs to be protected with flex conduit, but I'm unsure of which size is best. I and the homeowner prefer the look of the 5/16" vs. the 3/8" (i.e. less "chunky" looking) and the 5/16" allows a shorter bend radius (3-1/2" vs. 4" for the 3/8" FMC).
1) Southwire makes 5/16" flex metal armor, but I'm unsure if it is compliant with NEC 348.20. The NEC suggests that 3/8" is the minimum acceptable size, but if that's the case, why is 14-2 NM Romex manufactured with 5/16" metal conduit shielding?
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet226
2) If it is determined that 5/16" is code-compliant, it is even a good idea to use it? My concern is the availability of connectors that will work with this smaller diameter FMC and yet have a 1/2" male threaded end that will fit the 1/2" knock-outs on the fixtures.
3) The label on the 5/16" fmc says to not use set screw type clamps, which I assume is to prevent pinching the conduit and jeopardizing the wires. I guess "clamp-type" terminations are the best thing to use with 5/16"?
4) Can 5/16" FMC slip over sheathed 14-2 Romex or does the sheathing need to be stripped off before running the wires through the FMC?
Thanks
direct-wired lights/luminaries?
Background
Kitchen remodel and I'm the general contractor. I do not do any electrical work myself - the reason I ask this question is that my electrician is a little lazy and tends to use whatever materials are on his truck instead of making a trip to the electrical supplier to purchase and install the most appropriate materials for the application. Before he starts his final electrical work, I want to specify how and what materials should be used to hook-up the lights. Thus, I have a few questions regarding RWA FMC, line-voltage, direct-wire Zenon lights will be installed under the cabinets. I had the electrician make 14-2 drops at every fixture location. 14-2 wires are tied back into a j-box and are on a dedicated lighting circuit. I am aware that the 14-2 Romex needs to be protected with flex conduit, but I'm unsure of which size is best. I and the homeowner prefer the look of the 5/16" vs. the 3/8" (i.e. less "chunky" looking) and the 5/16" allows a shorter bend radius (3-1/2" vs. 4" for the 3/8" FMC).
1) Southwire makes 5/16" flex metal armor, but I'm unsure if it is compliant with NEC 348.20. The NEC suggests that 3/8" is the minimum acceptable size, but if that's the case, why is 14-2 NM Romex manufactured with 5/16" metal conduit shielding?
http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet226
2) If it is determined that 5/16" is code-compliant, it is even a good idea to use it? My concern is the availability of connectors that will work with this smaller diameter FMC and yet have a 1/2" male threaded end that will fit the 1/2" knock-outs on the fixtures.
3) The label on the 5/16" fmc says to not use set screw type clamps, which I assume is to prevent pinching the conduit and jeopardizing the wires. I guess "clamp-type" terminations are the best thing to use with 5/16"?
4) Can 5/16" FMC slip over sheathed 14-2 Romex or does the sheathing need to be stripped off before running the wires through the FMC?