why 277v circuit breakers ara bolt-on,
why not snap-in??
why 277v circuit breakers ara bolt-on,
why not snap-in??
Effectively their whole I-Line series is 'plug-in'.SQ D has 277V plug-in breakers, or at least they did.
Hi,
why 277v circuit breakers ara bolt-on,
why not snap-in??
I was told that higher fault-current rating of the equipment will dictate how the equipment is constructed. So the higher the fault-current rated equipment will have more support for the bussing and bolt-in style breakers.
Although the I-line equipment is plug-on, it has this feature design:
Breaker connections
are ?blow-on? type.
Under high-level fault
conditions, the magnetic
forces developed force
the jaws together,
gripping the bus bar
more firmly. Heavy-duty
jaw connectors are
plated to ensure good
conductivity at the
contact.
I was told that higher fault-current rating of the equipment will dictate how the equipment is constructed. So the higher the fault-current rated equipment will have more support for the bussing and bolt-in style breakers.
Interesting!
The information comes from the manufacturer, it is part of their normal marketing literature.Ditto, I wonder where this thought originated from? Did it come frpm the manufacturer. Which working for 2 major electrical manufacturers for 18 year I would have thought that would have been part of the selling points. But there were none. Why are there 'bolted pressure switches' rather than basic fusible disconnect switches?
The information comes from the manufacturer, it is part of their normal marketing literature.
http://static.schneider-electric.us...ay/I-Line and I-Line II Busway/0600DB1004.pdf