LO/TO of 4KV Switchgear

Status
Not open for further replies.

MBM76

Member
Location
NJ
We are discussing safe isolation of a 4KV switchgear at my workplace to allow maintenance and inspection on the buss and infeed cubicles. The switchgear normally operates single-ended, fed from one of the two infeeds. Both 4KV infeed lines and open and grounded, including the PT's.

My question is about whether or not the Buss Potential Transformer needs to be isolated to avoid the possibilty of backfeed?

Thanks
Mark
 

MBM76

Member
Location
NJ
We are discussing safe isolation of a 4KV switchgear at my workplace to allow maintenance and inspection on the buss and infeed cubicles. The switchgear normally operates single-ended, fed from one of the two infeeds. Both 4KV infeed lines and open and grounded, including the PT's.

My question is about whether or not the Buss Potential Transformer needs to be isolated to avoid the possibilty of backfeed?

Thanks
Mark

Failed to mention,
The buss is also grounded via a cubicle installed grounding truck.
 