Is it possible? I guess it is possible.

Can it be threaded to standard pipe thread sizes? No. To start with it is not the same dimensions as other pipes that are threaded to these standards.

Does NEC permit threading EMT? No, not threaded in the field anyway. Look at 358.28(B) Exception does allow for factory threaded integral couplings though.

Also 358.2 definition of EMT suggests it can not be threaded.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
I don't know if you are asking these questions for testing purposes or simply out of curiosity but the answers are in the NEC. Please try to find you answers there first and if you still have a question after looking at the Code, post it here and we will be happy to assist.
I am closing this thread.
 