Location
California
Facility has new OR LED lights. 120V circuit powers control panel that transforms to 24V DC that supplies power to the LED lights. Is the 24V from the control panel to lights considered a branch circuit?
 

steve66

Senior Member
Location
Illinois
Occupation
Engineer
No, I would say its not a branch circuit. But I'd say you need to follow the manufacturer's instructions for installation of the wiring.

Also, conduit may still be required for the wiring per 517.80.
 