Our head office recently experienced a 45 minute overvoltage when the local Utility (trying not to name names here) introduced 480/277V secondary when replacing pad-mount transformer to 208/120V wired building. I'm not a forensic engineer and may not find one in this forum, but as a licensed professional electrical engineer my company is asking for my advice. What types of things should I consider as possible points of damage other than the obvious equipment failures? Amazingly only a few copiers and fax machines were taken out and most PC's and other capital assets were seemingly okay. Do surge suppressors protect from this kind of overvoltage condition and are they compromised if so? Do I need to be concerned about building wiring integrity for potential future fires? Who/what type of entity should I get involved to check out the building systems other than insurance carrier?
Surge suppressors cannot protect against a prolonged overvoltage, even if that overvoltage rises above their clamping threshold in the first place.
However they may conduct enough current before failing that they trip other overcurrent protection which will then protect attached devices from the applied voltage. That is
not part of their design function, but can happen in some cases. And I would consider all of them potentially compromised. If they do not have an indicator that supposedly confirms that they are operating, they should be checked out for sure.
The power supplies in modern computing equipment are often designed for a wide range of supply voltages, and should in any case be able to protect the equipment they are powering even if they themselves fail.
Lighting ballasts, unless rated for multiple input voltages, may have been stressed to the point that there will be early failures down the road. Proximity sensors for lighting could be directly damaged.
Wiring will generally not be compromised since the insulation will be rated for 600V. The only potential damage would be from overcurrent during the high voltage condition, and I do not think you suffered from that.
Electric water heaters and other resistive heating elements which were operational during the outage may have their lives reduced because of hot spots in the resistive element which will eventually fail, and should probably be replaced.
Any devices powered by wall wart or brick external power supplies may have had those supplies compromised. Look for thermal damage indications at a minimum.
Those are just the ones that come to mind immediately. Hopefully one of the Forum members can give you a more specific recommendation on where to go from there.