We have a project in my office for which I was not the original designer. The project has a 600 KW Standby Generator and two 4-pole automatic transfer switches. I know we have to ground the neutral at the generator but all that is shown on the riser is a ground symbol connected to the generator. There is not really any details or detailed instructions just basically follow the NEC. So I want to make sure it gets done right so I am planning to provided instructions to drive a ground rod at the generator, and bond the neutral at the generator. If I am interpreting correctly, according to 250.58 I need to bond the ground rod at the generator to the building service grounding electrode system. The generator is located outside, about 50 feet from the building in a weatherproof enclosure. So do I need bond my generator grounding electrode to the building ground with a grounding electrode conductor sized according to 250-66? The generator and service transformer are located on opposite sides of the building but my ATS's are located in a room next to the main switchboard. Can I bring the GEC from the generator to the main switchboard ground bus?
The project is at a point where the building slabs have been poured so no way to easily get a conduit out of the building or the switchboard pad. Can I run the GEC from the generator with one of the feeders going to a transfer switch?