GFCI Labeling

Status
Not open for further replies.

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I have someone insisting that a receptacle that is GFCI protected VIA an upstream device has to be marked as GFCI protected. I say no. Am I having a senior moment?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Not required directly by the NEC but as Bob stated it cold possibly be part of the listing included in the instructions. I've never seen such a requirement.
 

Volta

Senior Member
Location
Columbus, Ohio
Are they thinking of 406.4(D)(2)(c)?

NEC said:
(c) A non?grounding-type receptacle(s) shall be permitted
to be replaced with a grounding-type receptacle(s)
where supplied through a ground-fault circuit interrupter.
Grounding-type receptacles supplied through the ground-fault
circuit interrupter shall be marked ?GFCI Protected?
and ?No Equipment Ground.? An equipment grounding
conductor shall not be connected between the grounding-type
receptacles.
 