Bonding a panel from the grounding bus bar acceptable?

Status
Not open for further replies.
Hi, I'm writing home inspection courses for development of a home inspection industry in Mexico.

This panel was bonded to the grounding bus bar instead of the neutral bus bar. I know it's not really right, but why would this be dangerous or unacceptable?
 

Attachments

  • P1190321.JPG
    P1190321.JPG
    107.1 KB · Views: 1
  • Bonding.JPG
    Bonding.JPG
    110.8 KB · Views: 1

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
IMO.

The black wire at the top of the ground bar is a violation.

There is no violation in running a wire from the ground bar to the pan.

Whether the N needs to be bonded or not is something that we cannot tell from the pictures.

There are 4 black wires coming in. One should be green or bare, and one should be white unless they are #4 or larger and are allowed to be marked as ground and N by strips of tape.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the two buses are separate, then the GEC needs to connect to the neutral bus not the EGC bus.
 

VA Jim

New User
It looks like the Lug at the top of the neutral bar has the hole that a bond screw would normally run through, I can see a wire with green tape, similar to the taping on the others, I zoomed in on the picture, it does come in with the others goes to top right side, along top, and down on left to ground bar, where the #3 arrow is. There is also a Bare #4 or #6 ? coming in from the bottom right to the bottom of the ground bar. I would be concerned that this is a sub-panel and has ground rods ( bare) and has a ground run with feeders. Bottom line is, I agree that more info is required, is it a sub-panel?, point of service?, Did an Inspector request the grounding be done this way? What kind of panel is it? It almost looks like the screw/ wire coming off the ground bar to the enclosure is to ground the can, due to how the ground bar is mounted. All that typing, and I still feel like I was no help.
 

kwired

Electron manager
Location
NE Nebraska
First question is whether this is a service or a feeder supplied panel?

Since there are 4 conductors in the supply it is probably a feeder, and the grounded conductor should not be bonded to anything else beyond the service disconnect.

If it is service equipment, why do we have a fourth conductor? It would be creating a parallel with the neutral and presenting us with other potential violations.

If this is not the service equipment or the main disconnecting means of a building or structure supplied by a feeder, or the first disconnecting means of a separately derived system, it does not need a GEC run to it. If this panel (with a separate EGC supplying it) does have a GEC run to it for any reason though, it lands on the EGC and not the grounded conductor bus.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
First question is whether this is a service or a feeder supplied panel?

Since there are 4 conductors in the supply it is probably a feeder, and the grounded conductor should not be bonded to anything else beyond the service disconnect.

If it is service equipment, why do we have a fourth conductor? It would be creating a parallel with the neutral and presenting us with other potential violations.

If this is not the service equipment or the main disconnecting means of a building or structure supplied by a feeder, or the first disconnecting means of a separately derived system, it does not need a GEC run to it. If this panel (with a separate EGC supplying it) does have a GEC run to it for any reason though, it lands on the EGC and not the grounded conductor bus.

maybe it is the service point the 4th wire coming in is the GEC. If so, shouldn't the conduit there be bonded?
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
My guess (educated) is this is a sub panel given that the grounds and neutrals are separate. Also because of the 4th (EGC) that is run with the feeders.
As such, the install is correct (assuming the bonding jumper is sized correctly).
The ground bus should bond to the cabinet and the neutral left floating.
 

kwired

Electron manager
Location
NE Nebraska
The OP asked a simple question that morphed into something not all that simple.
He has left out some important details, we must know if this is a service or feeder, or the first disconnect of a separately derived system. Depending on that answer there could be a few more details needed.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
He has left out some important details, we must know if this is a service or feeder, or the first disconnect of a separately derived system. Depending on that answer there could be a few more details needed.

a good example of why it is considered bad form to help DIYers here who just do not know all the questions, much less the answers.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
True, but there are many professionals that seem to lack the training you would hope they would have had also.

I suspect the main thing between professionals and others is that professionals tend to know what they don't know and are pretty good at learning what they don't know when needed. The amateurs do not know enough to know how little they know.
 

kwired

Electron manager
Location
NE Nebraska
I suspect the main thing between professionals and others is that professionals tend to know what they don't know and are pretty good at learning what they don't know when needed. The amateurs do not know enough to know how little they know.

I know you knew I knew what you knew...:lol:
 