AALZ, "Appliance and Utilization Equipment"
"If the equipment is only marked for use with conductors having a higher (75 or 90'C) temperature rating (wire size not specified), the 60'C ampacities (for circuits rated 100 A or less) and 75'C (for circuits rated over 100 A) should be used to determine wire size."
It appears I must size the wire for 60'C with no regard to the actual minimum rating of the components.
I think that I see the rationale for this, at first glance confusing, statement.
If the utilization equipment can be used with 60C wire, then using higher temp rated wire can be expected to provide higher ampacity
But if the equipment gets so hot on its own that higher temp wire MUST be used, then going to the higher ampacity rating would increase the temperature even more. Possibly above the insulation rating.
There would still be the separate parallel test that the current not exceed the terminal ratings. For this part the higher temp ampacity might be allowed.
Keep in mind that the UL language describes something for which 60C wire is not allowed. ("...only rated for higher temperature ....")