We have a project (expansion of ceramic factory), the client requests us to provide 3.5 core cable"reduced neutral" from transformer to panel & 3 core cable "without neutral" from panel to equipment's control panel, the client says "the control panel includes a transformer to step down the voltage level to the required level by the control circuits". We advised the client to continue using the 3.5 core cables every where because the order of the 3 core cables will be manufactured as a special order which might be more expensive than the order of the 3.5 core cable, aside from that we can utilize the unused neutral as a grounding conductor.
My question here, does the step down tr clear the harmonics of the control circuits? if no, so the neutral wire is necessary up to the control circuits. Please share your idea to find out the best solution.