smoke alarms on own circuit?

Status
Not open for further replies.

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
I don't have access to nfpa 72 @ the time. Do smokes have to be on own crk? If it matters it is a remodel.thanks

You are inviting the HO to defeat the alarms by turning off the breaker and removing the batteries to "shut them up" if you run them on their own circuit!:happyyes:
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Some local codes require them on their own breaker and others prohibit them from being on their own breaker.
 

kwired

Electron manager
Location
NE Nebraska
You are inviting the HO to defeat the alarms by turning off the breaker and removing the batteries to "shut them up" if you run them on their own circuit!:happyyes:

And if they would happen to not be ones with a battery, you just don't have any protection at all if the circuit is off for any reason and could go unnoticed for a long time. I like to put them on with some lighting circuit so that this will not happen.
 

RICK NAPIER

Senior Member
Location
New Jersey
2007 NFPA 72 Household Smoke Detectors
11.6.3 AC Primary Power Source.
The ac power source shall
comply with the following conditions:
(4) AC primary (main) power shall be supplied either from a
dedicated branch circuit or the unswitched portion of a
branch circuit also used for power and lighting.

and if not a household

4.4.1.4.1 Dedicated Branch Circuit. A dedicated branch circuit
of one of the following shall supply primary power:
 

iwire

Moderator
Staff member
Location
Massachusetts
2007 NFPA 72 Household Smoke Detectors
11.6.3 AC Primary Power Source.
The ac power source shall
comply with the following conditions:
(4) AC primary (main) power shall be supplied either from a
dedicated branch circuit or the unswitched portion of a
branch circuit also used for power and lighting.

and if not a household

4.4.1.4.1 Dedicated Branch Circuit. A dedicated branch circuit
of one of the following shall supply primary power:

When is a smoke alarm used outside a household?
 

construct

Senior Member
The ICCEC or Appendix 'K' of the IBC (if adopted) section K111.6 says; Single- and multiple-station smoke alarms required by this code and installed within dwelling units shall not be connected as the only load on a branch circuit. Such alarms shall be supplied by branch circuits having lighting loads consisting of lighting outlets in habitable spaces.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
2007 NFPA 72 Household Smoke Detectors
11.6.3 AC Primary Power Source.
The ac power source shall
comply with the following conditions:
(4) AC primary (main) power shall be supplied either from a
dedicated branch circuit or the unswitched portion of a
branch circuit also used for power and lighting.

and if not a household

4.4.1.4.1 Dedicated Branch Circuit. A dedicated branch circuit
of one of the following shall supply primary power:

When is a smoke alarm used outside a household?

Bob I think that you meant to ask about a smoke detector.
 

iwire

Moderator
Staff member
Location
Massachusetts
Bob I think that you meant to ask about a smoke detector.

Actually no, smoke detectors are for use with fire panels.

Smoke alarms are what we install in homes, at least that is how they are listed.

But you you did make me look at the posted code more carefully and now I wonder why that section says smoke detectors.


Single- and Multiple-station Smoke Alarms
(UTGT)

USE

This category covers single- and multiple-station smoke alarms intended
to be employed in indoor locations where sensitivity testing and maintenance
of alarms, per section 10.4.4 of ANSI/NFPA 72, ??National Fire Alarm
Code?? (2007), is required by code, Authorities Having Jurisdiction, or other
requirement.

This category also covers single- and multiple-station smoke alarms that
have been performance tested to a minimum 10-year extended battery life
under normal ambient conditions. Unless otherwise noted in the individual
Listings, the alarms are intended for flush-mounted installation only, and
are not intended for use on surface-mounted boxes.

This category also covers supplementary devices and accessories for use
with these units, such as a remote horn. These products are identified in the
individual Listings.


DETECTORS, AUTOMATIC FIRE
(UPLV)

These are either individual devices or prescribed combinations of
devices designed to detect flame, heat, smoke, or combustion gases resulting
from a fire and to automatically operate electrical signaling contacts.
The signaling contacts may be integral parts of an individual device or
parts of a separate device to which the detecting element is connected as
an extended component.

The signaling contacts of the detector are intended to be connected to
the circuit conductors of fire protective signaling systems recognized by
the National Fire Protection Association Standards, so that the fire alarm
signal initiated by the detector will be indicated by the system.
 