Im helping someone with a design that is uncomfortably un-familar for me. We have some fixed load bakery equipment that we are required to run through a phase converter to power a few pieces of equipment. The phase converter is feeding a panel and the panel feeds the equipment. I have used a phase converter on more then one occasion but for a panel.
Input to the phase converter is 78A @ 240-1 or 18.72 kW
Output voltage is 208-3
The loads are "fixed" in my opinion.
Conductor Sizing:
According to 455.6 (A)(2)
"The conductors shall have an ampacity of not less then 250% of the sum of the full load" (Im assuming this is single phase full load)
So 78A * 2.5 = 195 A so the conductors must be sized for 195A, therefore 3/0 CU will be OK.
NEXT
MOCP:
455.7 (B) requires the conductors to be protected in accordance with their ampacity therefore a 200A CB will be adequate. The problem is that the single phase panel that is feeding the converter is a 100A panel!
Does all this seem correct?