I am trying size the primary feeders on a dry type transformer. To help with coordination and per Table 450.3(B) we are sizing the primary OCP at 250% (secondary is at 125%). My question is, are the primary feeders sized to 250% or 125% of the primary FLA?
Sizing the feeders to 250% FLA will match the over-current rating and is not wrong. I wonder if you could size the feeders to 125% and treat the transformer more like a motor. I cannot find anything on primary feeders in the NEC.
Thanks.