Is there an NEC article that addresses an equipment grounding conductor to the utility transformer?
I have a building that has a 600 amp 3phase 480/277v service and has an equipment grounding conductor from the utility transformer that is going through the grounding bushings and is landed on the neutral bar. The connection between the neutral and the equipment is just the jumper strap.
I have the same issue on the load side of this equipment. The equipment ground conductor is connected to the neutral bar and is looped through the ground bushings to an MCC.
Should the EGC be run to the utility transformer?
Is there a code article for this or is this the utility standard? I have never run an EGC to a utility transformer. I have seen engineers do this on the drawings, but we have never installed it this way.
We are supose to correct the grounding on this job for a VFD installation.
I have a building that has a 600 amp 3phase 480/277v service and has an equipment grounding conductor from the utility transformer that is going through the grounding bushings and is landed on the neutral bar. The connection between the neutral and the equipment is just the jumper strap.
I have the same issue on the load side of this equipment. The equipment ground conductor is connected to the neutral bar and is looped through the ground bushings to an MCC.
Should the EGC be run to the utility transformer?
Is there a code article for this or is this the utility standard? I have never run an EGC to a utility transformer. I have seen engineers do this on the drawings, but we have never installed it this way.
We are supose to correct the grounding on this job for a VFD installation.