jahilliard
Senior Member
We install the services and Control panels for decorative lake fountains all the time...I'm sure we have done 100 or more and will do another 50 in the next few months. Of all that we have done only 2 have been turned down because they didn't comply with Art. 682...specifically section 682.11 "Service Equipment shall disconnect when the water level reaches the height of the established electrical datum plane." I'm curious has anyone else experienced this scenario and I am also curious as to how you were able to comply with the requirement. We did come up with a solution but it seemed rather ridiculous and it was a home made installation that most likely wasn't able to meet any type of UL listing. For the most part I'm frustrated because meeting this requirement just doesn't seem practical seeing as how in every case we have our service installed adjacent to a transformer sitting on the ground servicing several bldgs or homes and if the water level were to reach a dangerous level there would be much more dangerous scenarios than our little service. Our electrical is for a decorative fountain...it doesn't control the water level in any way. I could understand if it were intended to be a safety limit type thing but this isn't the case. Just looking for some feedback on the Article and maybe a creative solution to meeting the requirement. Thanks