Wired a press brake at a machine shop, 3 phase 20 amp 460 volt unit. Basically a hydraulic pump. It is a very large unit bolted to the floor. The machine shop had driven a ground rod behind the machine and had me connect a wire to the frame. The machine was used and did not have installation literature.

My question is why connect a ground rod at each machine? If it an issue of static buildup why not ground to building steel or back to the panel?
 

iwire

Moderator
Staff member
Location
Massachusetts
A lot of machine shop equipment has computer control and the data lines were RS232 or similar that use a ground refrerance this could cause unwanted current on the data lines and data transfer failure.

People found the 'solution' was to float the macine from the EGC and put in a ground rod instead. Of course this is dangerous and a code violtion.

Legitimate solutions are isolating devices in the data lines

I think this has carried over into thinking machines need ground rods. :roll:
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
It would end being something like this which as other have stated will do no harm but will provide no benefit either. This is now called an auxiliary electrode.