GFCI NEEDED

Status
Not open for further replies.

jumper

Senior Member
422.52 Electric Drinking Fountains. Electric drinking fountains
shall be protected with ground-fault circuit-interrupter
protection.

Wait you said under. Does the receptacle feed/serve the fountain?
 
Last edited:

kwired

Electron manager
Location
NE Nebraska
422.52 Electric Drinking Fountains. Electric drinking fountains
shall be protected with ground-fault circuit-interrupter
protection.

Wait you said under. Does the receptacle feed/serve the fountain?

That is only section that relates GFCI directly to a drinking fountain and is for the drinking fountain only - and has no voltage or current limitations attached.

If a nearby receptacle not associated in any way with the fountain is present then we have to go back to 210.8 to see if any other conditions would make GFCI necessary.
 