Other factors need consideration, like is the load able to be increased during "normal operation", or sometimes a motor is derated because of frequent starting, reversing, plugging, etc.I though as a rule of thumb when taking a amp reading on motors if the motor has amp draw of 50% or less that it is not efficient and a smaller motor should be sized. Is this correct ? How would one determine when a motor is oversized for a application ?
Not based on a single reading.I though as a rule of thumb when taking a amp reading on motors if the motor has amp draw of 50% or less that it is not efficient and a smaller motor should be sized. Is this correct ? How would one determine when a motor is oversized for a application ?
Honestly, there is a load range of a motor where the PF is indicative of how much the motor is loaded. Beyond a 50% load on this specific motor below, the PF change is not a good indication of the motor load. Please see below:From the title of the thread, I have to ask whether you know that the PF of a motor has nothing to do with how heavily it is loaded during normal operation. The PF does vary with motor loading, but if a motor is only loaded to 50% of its capacity, that does not tell you that the PF is 50%. Forgive me if I have belabored a point that you already understood, but since you did put PF in the title of the thread, I thought I would probe a bit.
OP had it as 50% current, not 50% capacity.but if a motor is only loaded to 50% of its capacity,
I take readings on motors for the company and it seems like it is for nothing . I have very limited knowledge about checking on motors and I ask these questions to gain some knowledge on this forum about this subject. I picked up 50% somewhere as limit of a oversized motor and poor pf. Poor PF. to me means a motor oversized for the job, wasted power. And yes I would guess it would be more than one reading to determine such.
Thanks for the help here.
Seems like contradictory statements......From the title of the thread, I have to ask whether you know that the PF of a motor has nothing to do with how heavily it is loaded during normal operation. The PF does vary with motor loading..........
Let's start with this statement. It may seem like "nothing" to you if you are only being asked to do the work of taking the readings. But for someone like a maintenance planner, this could be vital information, if only as a baseline and later for comparison AGAINST that baseline. So for example if the Mtc planner knows the flow of a pump, and over 3 years he sees that at a given flow the motor power requirement is increasing, that can tell him that the bearings are wearing out. Or if it's a conveyor and the power requirement is decreasing without there being a decrease in load, it could mean a belt is slipping.I take readings on motors for the company and it seems like it is for nothing . I have very limited knowledge about checking on motors and I ask these questions to gain some knowledge on this forum about this subject. I picked up 50% somewhere as limit of a oversized motor and poor pf. Poor PF. to me means a motor oversized for the job, wasted power. And yes I would guess it would be more than one reading to determine such.
Thanks for the help here.