3 Phase 480VAC Emergency Generator Cable installation?

Status
Not open for further replies.

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I don't see a problem there but what about 300.3(B)(1) . The exception does not seem to apply here because the raceway does not appear to be plastic. Sorry I show my ignorance here but it doesn't look correct to me
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
I think you have to run all the circuit conductors together in the same pipe.

I don't think the "crossing" is an issue.

Looks like a very small bonding wire.
 

texie

Senior Member
Location
Fort Collins, Colorado
Occupation
Electrician, Contractor, Inspector
I don't see a problem there but what about 300.3(B)(1) . The exception does not seem to apply here because the raceway does not appear to be plastic. Sorry I show my ignorance here but it doesn't look correct to me

Little hard to tell for sure from the photo, but this looks like an MI cable install and it looks like there is a non-ferrous mounting plate for the cables. Looks OK from here. I will say that those bonding jumpers look light as compared to the cable size, but that is just a guess from what I see in the photo.
 

CIECO

Senior Member
Not good in my book

Not good in my book

Think eddy currants you have a problem if there is any steel between phases.
 