250.24 and 250.30 Confused

Status
Not open for further replies.

VIC1958

Senior Member
Can someone please help me deciphering the difference between these two section as it relates to where the GEC bonds to the neutral in a residential application. 250.24 states from what I see, the GEC can be bonded to the neutral at several areas, service drop, meter can or at the panel board. In 250.30(A)(1) says the GEC needs to be bonded to the neutral at the first system disconnection means. I know of certain municipalities that follow 250.30 and I know of others that state the GEC must bond to the neutral lug in the meter can no mater what. Thanks for any input.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
250.24 is pertaining to the service, 250.30 is pertaining to a Separately Derived System

Roger
 

VIC1958

Senior Member
Thanks Roger, I guess my confusion starts with the definition of a Separately Derived System.... I understand batteries, solar, wind, etc. But how do transformers play into it, if the premise wiring system is being fed by a transformer. Pardon my ignorance.
 

kwired

Electron manager
Location
NE Nebraska
Thanks Roger, I guess my confusion starts with the definition of a Separately Derived System.... I understand batteries, solar, wind, etc. But how do transformers play into it, if the premise wiring system is being fed by a transformer. Pardon my ignorance.
If the secondary of the transformer is not connected to any part of the primary (before any bonding for equipment grounding purposes is done) then it is separately derived. In other words it does not depend on any of the primary portion to derive its output voltage.

An autotransformer has a current carrying connection that is common to both primary and secondary coils, and this would not be a separately derived system.

Most general use transformers are separately derived systems.
 

VIC1958

Senior Member
So it can be assumed most of the time that utility owned transformers feeding residential units are a separately derived system, generally speaking. Also, that the dwellings grounding electrode/GEC can be bonded to the neutral at any point from the transformer and the first point of disconnection at the house?
 

kwired

Electron manager
Location
NE Nebraska
So it can be assumed most of the time that utility owned transformers feeding residential units are a separately derived system, generally speaking. Also, that the dwellings grounding electrode/GEC can be bonded to the neutral at any point from the transformer and the first point of disconnection at the house?

They are separately derived from the primary distribution. For NEC applications though the transformer itself is not covered if it is on the supply side of the "service point" and what you first encounter in a utility supplied system that is covered by NEC is usually called "Service conductors" whether it be service lateral, service drop....

GEC must be bonded to service equipment somewhere on the premises side of the service point, and at very least at each structure served if there are multiple structures involved in the distribution of the customers portion of the service conductors.
 

roger

Moderator
Staff member
Location
Fl
Occupation
Retired Electrician
So it can be assumed most of the time that utility owned transformers feeding residential units are a separately derived system, generally speaking. Also, that the dwellings grounding electrode/GEC can be bonded to the neutral at any point from the transformer and the first point of disconnection at the house?

Vic, these illustrations may help clear it up.

Service Grounding 250.24

1113854601_2.jpg


Separately Derived System

1113856452_2.jpg



Roger
 

david

Senior Member
Location
Pennsylvania
Referencing NFPA 70/2008
I might not understand what you?re asking but I think you are confusing the allowable connections of the Grounding electrode conductor to the grounded conductor (neutral) in 250.24 (A)

With the mandated bonding location of the grounded service conductor (neutral) found in 250.24 (C)
 

kwired

Electron manager
Location
NE Nebraska
I see the picture of the service installation has ungrounded conductors entering the weatherhead, but no ungrounded conductors anywhere else:cool:

Vic, these illustrations may help clear it up.

Service Grounding 250.24

1113854601_2.jpg


Separately Derived System

1113856452_2.jpg



Roger
 

shortcircuit2

Senior Member
Location
South of Bawstin
Yes that could be dangerous with those short ungrounded conductors...

In Mike's photo of an AC service it implies that there are only 3 options for a connection point of the GEC. Let me point out that there could be a trough between the meter and the service disconnect(s) where the GEC could also connect to the grounded conductor.
 

Smart $

Esteemed Member
Location
Ohio
Can someone please help me deciphering the difference between these two section as it relates to where the GEC bonds to the neutral in a residential application. 250.24 states from what I see, the GEC can be bonded to the neutral at several areas, service drop, meter can or at the panel board. In 250.30(A)(1) says the GEC needs to be bonded to the neutral at the first system disconnection means. I know of certain municipalities that follow 250.30 and I know of others that state the GEC must bond to the neutral lug in the meter can no mater what. Thanks for any input.
I think you are confusing, just a tad, between the GEC connection(s) and the main or system bonding jumper...

Regarding a service, the main bonding jumper (MBJ) must be located in the service disconnecting means. The MBJ is the connection between the grounded service conductor and the equipment grounding system (EGS, to which EGC's are connected). At the location of the MBJ, any GEC can be connected to either side of the MBJ, i.e. the grounded (neutral) conductor or the EGS bus.

A separately derive system (SDS) is similar, but the equivalent of an MBJ for service is called a system bonding jumper (SBJ). The SBJ can be either in the source or first disconnecting means enclosure. The GEC(s) can be connected to either end of the SBJ wherever the SBJ is located... but IIRC it(they) can only be connected to the grounded (neutral) conductor at or ahead of the SBJ... not on load-side of the SBJ.
 

kwired

Electron manager
Location
NE Nebraska
Yes that could be dangerous with those short ungrounded conductors...

In Mike's photo of an AC service it implies that there are only 3 options for a connection point of the GEC. Let me point out that there could be a trough between the meter and the service disconnect(s) where the GEC could also connect to the grounded conductor.
There could be a gutter or splice box ahead of the meter also and the GEC could land there as well.
 