Can we place an UPS with built in batteries in lab area? i understand the battery is hazard element but how about the built in batteries. The issue raised when the client refered to an supplier & the supplier confirnmed the need of UPS for lab equipments & said the lab equipments will be damaged during power failure in absence of the UPS, in line with that we don't have any free space to place that UPS.
Most of the UPS systems I've dealt with us VRLA batteries. Valve regulated lead acid but more commonly called sealed lead acid.
This an excerpt from the spec of the ones we use:
These batteries are classified as non-spillable because they have been shown to meet the requirements of Packing Instruction 806.
Special Provision A67, contained in IATA Dangerous Goods Regulations and the ICAO publication, Technical Instructions for the Safe Transport of Goods by Air and states that:
"Non-spillable batteries are not subject to these Instructions if, at temperature of 55? C, the electrolyte will not flow from a ruptured or cracked case and there is no free liquid to flow and if, when packaged for transport, the terminals are protected from short circuit."
These batteries were classified as meeting the A67 requirement after testing by PIRA, who stated that the batteries may be regarded as non-dangerous. Several other independent internationally recognised laboratories are also in agreement that these battery types are non-dangerous.
In meeting the requirements of packaging instruction 806 and Special Provision A67 the subject batteries may be regarded as non-dangerous