XFMR secondary fusing-dual application?

Status
Not open for further replies.

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
You could read article 450.3 as based on using the branch feeder protection as the transformer secondary protection.
Conductor protection is a requirement. Transformer secondary protection is optional.
 