ewj1999

New member
When crossing a building epansion joint with a rack of conduit suspended by allthread and where the conduit 90's away from the rack out to a piece of equipment or device is an expension fitting required? The thought process being that the conduit rack is suspended, not rigidly fastened to the structure.
 

GoldDigger

Moderator
Staff member
Location
Placerville, CA, USA
Occupation
Retired PV System Designer
If there were not a building expansion joint, I would consider whether the raceway after the 90 was long enough and flexible enough (including supports) to accommodate the calculated expansion.

Sent from my XT1080 using Tapatalk
 