John120/240
- Olathe, Kansas
There is no code for temporary lights that I know of. You need enough light to get your job done.
Is there code for installing light stringers regarding distance apart etc.?
Sent from my iPad using Tapatalk
Anyone have a rule of thumb they use for figuring out how many 50 or 100' light stringer they use for a space....sq ft etc. ? Thanks
Have not done much renovation work. If you have a commercial space about 25k sq ft and it will be a complete gut(demo). What do you usually use for temp light? Light stringers and stands? Thx
Stringers are made up of 12/3 NM cable with one lighting and one power circuit. Here's some regional lingo, the lamp is installed in a left handed socket and the power is from a laundry drop.
In my opinion that is still an NEC violation.
You have lights and receptacles on the same MWBC.
590.4(D) Receptacles.
(1) All Receptacles. All receptacles shall be of the ground-
ing type. Unless installed in a continuous metal raceway
that qualifies as an equipment grounding conductor in ac-
cordance with 250.118 or a continuous metal-covered cable
cordance with 250.118, all branch circuits shall include a
separate equipment grounding conductor, and all recep-
tacles shall be electrically connected to the equipment
grounding conductor(s). Receptacles on construction sites
shall not be installed on any branch circuit that supplies
temporary lighting.
In this case you would have two branch circuits so no violation.
What would be the reasoning for not allowing such an installation ?
Are those incandescent bulbs exempt from the ban?
I would imagine that left handed LEDs and CFLs may not be available.
Sent from my XT1080 using Tapatalk
Next comes where and when does it apply?osha standard 1926.56 (a) deals with construction lighting , 5 foot_candles at any given spot
Sent from my SGH-T889 using Tapatalk
Who provides light for the guys installing the temporary lighting?
They need safety also.
No, you would not have two branch circuits, you would have a single MWBC.
Kitchen counter requires two branch circuits, run one 12-3. Equals two branch circuits. Temp light/power same thing.
Something to back your statement up:Kitchen counter requires two branch circuits, run one 12-3. Equals two branch circuits. Temp light/power same thing.
(A) General. Branch circuits recognized by this article shall be permitted as multiwire circuits. A multiwire circuit shall be permitted to be considered as multiple circuits. All conductors of a multiwire branch circuit shall originate from the same panelboard or similar distribution equipment.