Are the "main" and "tie" breakers in the attached coordination curve coordinated?
I'm specifically looking at the vertical sections of the purple and blue curves where they pretty much overlap 100%. If I'm reading this curve right, considering a fault of about 950 amps, the purple breaker will start to operate at about 0.25seconds and will not clear until about 9 seconds. Meanwhile, the blue breaker will start to operate at about 0.45 seconds, so that the two are not coordinated.
Also, is the clearing time really almost 9 seconds in this region? Seems like a long clearing time.
I'm specifically looking at the vertical sections of the purple and blue curves where they pretty much overlap 100%. If I'm reading this curve right, considering a fault of about 950 amps, the purple breaker will start to operate at about 0.25seconds and will not clear until about 9 seconds. Meanwhile, the blue breaker will start to operate at about 0.45 seconds, so that the two are not coordinated.
Also, is the clearing time really almost 9 seconds in this region? Seems like a long clearing time.