I want to run a cable (I assume we'll be using some multiconductor cord for extra hard usage) from a type z purged enclosure to a solenoid valve listed for GP in C1D2. The surrounding is a C1D2 area.
Since the valve's enclosure is not required to be explosionproof and the fact that it comes with a listed cable plug, no sealing fitting is required on this side, right?
And also: per NEC 501.15(E)(1) Excp. 1 and NFPA 496 4.3.4 I don't need sealing fittings for cables leaving the enclosure. Just ordenary cable bushings to maintain the pressure inside the enclosure. Correct?
Now NEC 501.10(B)(2)(5) asks for listed fittings for extra hard usage cords. Do I need listed fittings under these conditions?
Daniel