I was involved in a generator installation where the electrical contractor had installed a 1600A ATS next to a 1000KVA utility transformer, in the same room. Line voltage was 480V. The ATS was connected to the Trafo with 4x600MCM conductors per phase. There was no disconnect or overcurrent protection between the equipment and the ATS does not have a service disconnect in it.
Contractor tells me Article 721 allows this. I am worried that 1) there is no protection for the ATS in the event it closes onto a fault current, and 2) there is no way to test the ATS works, 3) no way to do maintenance on the ATS. Am I being too cautious, is the contractor correct?