overkill94
Member
- Location
- California
I'm doing an inspection on a large piece of equipment that has a conduit drop from the ceiling with SOOW cord pulled through it. I wrote them up for the conduit fill being exceeded (10/4 SOOW through 1 1/2" RMC) and they're planning on stripping the outer insulation and pulling the conductors through the conduit without the outer jacket. Is there anything in the code restricting the use of SOOW cord through conduit in general? If not, would this be an acceptable solution?