system grounding through meteal water pipe???

Status
Not open for further replies.

Toros

Senior Member
Location
Tujunga, CA
hi,why we bound metal water pipes (primary sys. grounding) as soon as they enter in to the building (within 5 ft)? How would you ground the system if there was no metal water pipe into the building?????? I am still not stuck there.... thank you
 

Ponchik

Senior Member
Location
CA
Occupation
Electronologist
If new construction or you have access to the rebar then you can use it as an electrode with a minimum of 20' contact with the foundation (does not have to be continuous 20'). Otherwise a common practice is (2) ground rod with minimum earth contact of 8' each.

(NEC 2011) 250.50 has the details
 